• If you're struggling to login because of the verification email not reaching you, don't worry it's just the forum settings applying the change slowly. I'll get in touch with those who are awaiting the verification email and sort your accounts out. I think new ones should go through fine now in most cases.

EF: Socket on spur with cable in conduit

Currently reading:
EF: Socket on spur with cable in conduit

G

GrahamP

Socket on spur with cable in conduit

Hi. I'm hoping someone can help with a question about adding a socket as a spur onto a ring mains circuit (rcd protected at CU).
Its a 2 gang socket so max load could be 26A. The 2.5 TE cable is rated for 27A but this reduces to maybe 20A if its in buried in a wall in conduit (as it will be). Its not a long run (500 mm) and its unlikely anyone is going to plug two electric heaters into it, but would is this something to worry about? Would it be OK/advisable to label as, perhaps, max 13 A total load? many thanks.

Socket on spur with cable in conduit to Continue reading...