• If you're struggling to login because of the verification email not reaching you, don't worry it's just the forum settings applying the change slowly. I'll get in touch with those who are awaiting the verification email and sort your accounts out. I think new ones should go through fine now in most cases.

EF: Plazma cutter causing SPD failure??

Currently reading:
EF: Plazma cutter causing SPD failure??

A

Andy Y

Plazma cutter causing SPD failure??

I've just had a potentially nasty issue involving a Burnt out, type 2 SPD. My customer has been using a small plasma cutter,
I don't have the exact details of the unit to hand, but it does plug in to a standard 13a socket outlet This is a new 100a single phase TT supply to a small commercial unit.
This was a very close call. The SPD, located directly next to the consumer mainswitch, had burnt out to such a degree, that it has (fortunately) taken out the fuse at the intake.
Is it possible, this cutter could produce enough transient voltage to create this issue?
I was led to believe, these devices should go open circuit when they fail.

Plazma cutter causing SPD failure?? to Continue reading...

ElectriciansForums.net for the latest in electricians' jobs, news, advice and more
 
Back
Top