• If you're struggling to login because of the verification email not reaching you, don't worry it's just the forum settings applying the change slowly. I'll get in touch with those who are awaiting the verification email and sort your accounts out. I think new ones should go through fine now in most cases.

EF: Pat testing - low insulation reading

Currently reading:
EF: Pat testing - low insulation reading

T

tomodo

Pat testing - low insulation reading

Hi all, recently pat tested abit of equipment, it contains 24v power supplies, a frequency inverter, relays and a motor, its on a 13amp plug so requires pat test, however we get a low LN to E reading unless we disconnect the inverter. Reading is 0.9Mohms, is this normal or should you still requires the minimum 1Mohm resistance to earth. Thanks