• If you're struggling to login because of the verification email not reaching you, don't worry it's just the forum settings applying the change slowly. I'll get in touch with those who are awaiting the verification email and sort your accounts out. I think new ones should go through fine now in most cases.

EF: External lighting around perimeter of Sports Complex

Currently reading:
EF: External lighting around perimeter of Sports Complex

C

cliffed

External lighting around perimeter of Sports Complex

Recently did an EICR on external lighting, installed in the early 70’s, never been tested before & never compliant.
The Swa’s are 2.5 x2 core entering in a recently new Cut Out.
The problem the Client as now is that @ least 4 lighting points have high Zs reading over 10 ohms.
Installing new Swa to these positions are gonna be problematic.
The easier option if possible would be to protect these 4 light points with a 30 ma Rcd, rather a Temporary fix @ this moment.
Or disconnection of these lights not gonna be popular there.
Any ideas my comrades

External lighting around perimeter of Sports Complex to Continue reading...