• If you're struggling to login because of the verification email not reaching you, don't worry it's just the forum settings applying the change slowly. I'll get in touch with those who are awaiting the verification email and sort your accounts out. I think new ones should go through fine now in most cases.

EF: Discrimination

Currently reading:
EF: Discrimination

D

Download Virus

Discrimination

First post - Go easy!

Advice please - suggestions/best practice.

Domestic property, TNCS supply, 25mm tails to RCBO C/U with 100A main switch.

I want to install a distribution circuit from the aforementioned C/U (I dont want to split tails) to supply a second RCBO C/U (essentially a garage board), serving little more than a lighting and power circuit.

The cable supplying the second board is 10mm T&E and already buried within the fabric of the building and will be used (non negotiable).

with discrimination in mind, what device should I be terminating the 10mm distribution cable, within the second board?

I am using Fusebox boards and the smallest main switch I can see is 63A. This is too big for the 10mm supply cable???

Any advice warmly recieved.

 Thanks

Discrimination to Continue reading...