• If you're struggling to login because of the verification email not reaching you, don't worry it's just the forum settings applying the change slowly. I'll get in touch with those who are awaiting the verification email and sort your accounts out. I think new ones should go through fine now in most cases.

EF: ASHP Supply & CU Setup

  • Thread starter TurnerElectrical
  • Start date

Currently reading:
EF: ASHP Supply & CU Setup

T

TurnerElectrical

ASHP Supply & CU Setup

Evening all,

Just after a sense-check before I commit & send the quote.

I’ve been asked to run in an SWA to feed a small CU that’ll sit inside an extension on the side of the house for the ASHP from a Tesla Gateway.

The customer has said the heat pump guys have asked for 2x 16A & 1x 6A circuits for the heat pump, immersion & control gear.

My plan was to fit a 40A C Curve MCB in the Tesla Gateway, run in the 10mm SWA (roughly 15m) then one of these (FuseBox RTB630302M DP RCD TYPE B 63A 30mA - https://www.fusebox.shop/products/fusebox-rtb630302-dp-rcd-a-type-63a-30ma) as a main switch in ASHP CU to satisfy the Type B RCD that Valliant ask for & then have 3x MCBs for the 3 circuits (1x 16A C Curve for the heat pump, 1x 16A B Curve for the immersion & 1x 6A B Curve for the control gear).

Does that sound about right?! I haven’t done an ASHP supply before.

ASHP Supply & CU Setup to Continue reading...